Pellet Fan

Please login or register.

Login with username, password and session length
Advanced search  

News:

Welcome to Pellet Fan!

Pages: [1]   Go Down

Author Topic: Any electricians here? 3 Phase question.  (Read 1703 times)

0 Members and 1 Guest are viewing this topic.

BigDave83

  • Friends Want you to cook way to much.
  • ******
  • Offline Offline
  • Posts: 2270
  • South West PA
Any electricians here? 3 Phase question.
« on: November 20, 2020, 04:14:32 PM »

one of the GF's friends wants to start a pizza shop, I found a nice used 208V (I think) 3 phase unit. Bakers Pride counter top double deck. I looked at their website and found a manual for one. Not sure if it is the same model. But it shows either or, now i don't know if it needs o be ordered either or or i you just pull some jumper wires out on the single phase unit.

 Anyway I was looking for a converter or even instruction on building one. But everything I have come across shows a converter that seem to be used with a piece of equipment having  motor on it. There is no motor on this oven. I will try to post pictures of the connections in the manual here.

 does anyone know what i would need to run this of singe phase? or am I better off searching and waiting until I find a single phase unit. Gas would be a better option but electric will be easier to get going for him currently.
 

Thank you.

3 wire
https://www.screencast.com/t/cQMi6dZl95

4 Wire
https://www.screencast.com/t/5n94GEt3Yjq


Ultimately he wants to start a trailer or truck do sell pizza and also ice cream.
Logged

02ebz06

  • Friends Want you to cook way to much.
  • ******
  • Offline Offline
  • Posts: 2625
  • Rio Rancho, NM
Re: Any electricians here? 3 Phase question.
« Reply #1 on: November 20, 2020, 04:39:57 PM »

I'm no electrician, although I've done a lot of electrical work, single phase only.
But, since no motor is involved, I'm guessing the reason for three phase is to handle the current for all the heating elements.
If you look at one of the wires, think three times that size if it was single phase.
Same for the circuit breaker, for example, a 3-phase breaker at 60amp per leg would require a 180amp breaker for a single phase circuit.
Not ideal, if it even meets code.

If nobody here can help, I'd suggest going to the PizzaMaking forum.
There are a couple people currently building out pizza restaurants there.
You could ask your question there and maybe they could help (or ask their electricians  ;D)
I know there are posts about the Bakers Pride ovens, but not sure if any involved electrical questions.

EDIT:  Got to thinking, why would he want to convert to single phase anyway?
         Cost of running heavier wire and bigger breaker would most likely cost more money.
 
« Last Edit: November 20, 2020, 04:58:29 PM by 02ebz06 »
Logged
Bruce here - These are my cooking toys:
Lone Star Grillz 20x42 Pellet Grill (on order),   CampChef XXL Vertical Pellet Smoker,   Grilla Grills Primate (on order),   Pizza Party Emozione pizza oven

hughver

  • Friends Want you to cook way to much.
  • ******
  • Offline Offline
  • Posts: 2198
  • University of Louisiana
Re: Any electricians here? 3 Phase question.
« Reply #2 on: November 20, 2020, 05:32:40 PM »

Do you have a model number?
Logged
--Hugh -- Sun Lakes, AZ. Traeger Select W/SS4, BGE-L, Charbroil Inferred Gas, Smokey Mountain Vertical Gas

BigDave83

  • Friends Want you to cook way to much.
  • ******
  • Offline Offline
  • Posts: 2270
  • South West PA
Re: Any electricians here? 3 Phase question.
« Reply #3 on: November 20, 2020, 08:26:57 PM »

Do you have a model number?

It is either a P22 or P48. I believe it is a 22 though.
Logged

BigDave83

  • Friends Want you to cook way to much.
  • ******
  • Offline Offline
  • Posts: 2270
  • South West PA
Re: Any electricians here? 3 Phase question.
« Reply #4 on: November 20, 2020, 08:32:07 PM »

I'm no electrician, although I've done a lot of electrical work, single phase only.
But, since no motor is involved, I'm guessing the reason for three phase is to handle the current for all the heating elements.
If you look at one of the wires, think three times that size if it was single phase.
Same for the circuit breaker, for example, a 3-phase breaker at 60amp per leg would require a 180amp breaker for a single phase circuit.
Not ideal, if it even meets code.

If nobody here can help, I'd suggest going to the PizzaMaking forum.
There are a couple people currently building out pizza restaurants there.
You could ask your question there and maybe they could help (or ask their electricians  ;D)
I know there are posts about the Bakers Pride ovens, but not sure if any involved electrical questions.

EDIT:  Got to thinking, why would he want to convert to single phase anyway?
         Cost of running heavier wire and bigger breaker would most likely cost more money.


The building is wired single phase, the oven is 3 phase, so we are looking go single to 3 phase. He is a long ways off, but would like to get an oven and maybe start doing some stuff, so we can feed the people that are coming to help him remodel. The place is in bad shape, as it set empty for a good while, the equipment that was there I think the realtor went in and pulled it all out. with out the owners knowledge.
Logged

W6YJ

  • Starting to taste the Smoke.
  • ***
  • Offline Offline
  • Posts: 221
Re: Any electricians here? 3 Phase question.
« Reply #5 on: November 20, 2020, 10:20:58 PM »

According to their website, they are available in either single or three phase.
As they only draw 3600 Watts, if it is re-configured for single phase, it would need ~16 amps.
The manual shows jumpering for either single or three phase operation.
Logged

BigDave83

  • Friends Want you to cook way to much.
  • ******
  • Offline Offline
  • Posts: 2270
  • South West PA
Re: Any electricians here? 3 Phase question.
« Reply #6 on: November 21, 2020, 07:58:23 AM »

According to their website, they are available in either single or three phase.
As they only draw 3600 Watts, if it is re-configured for single phase, it would need ~16 amps.
The manual shows jumpering for either single or three phase operation.

I was looking at the wiring diagrams and saw the jumpers. The used one i found the guy says it is 3 phase, I wondered if I bought it I could reconfigure the wiring going adding jumpers or if I could figure out how to make something to run it off the single phase wiring in the building.
It is about a 2 hour drive to where it is at. It may be wise to see if there is a serial number and then call Bakers pride and question them on how it may be wired. I had not thought of that until now.
Logged

WiPelletHead

  • Digging the Pellet Smoke.
  • ****
  • Offline Offline
  • Posts: 298
  • Mondovi WI
Re: Any electricians here? 3 Phase question.
« Reply #7 on: November 21, 2020, 08:09:30 AM »

Google "can a 3 phase pizza oven be converted to single phase"

You will get quite a few hits. Looks like it can be done.
Logged
Weber Searwood 600

Mikro

  • Starting to taste the Smoke.
  • ***
  • Offline Offline
  • Posts: 223
Re: Any electricians here? 3 Phase question.
« Reply #8 on: November 21, 2020, 10:48:21 AM »

My  :2cents: here:
If the oven is 3 phase and you want to use single phase, then you may need either a VFD variable frequency drive or a rotary phase converter. I am NOT an electrician, so I am not sure these would work for the oven as they are used for motor operations.
That being said, since it is an electrical function of the temp being controlled by wattage/amperage, which may be similar to variable speed of a motor. this may equate to frequency?

Maybe contact some of the VFD manufactures and see what they say?

Just another outside of the box thought, not intended to be correct without confirmation. :)
MK
Logged
Firecraft Q450
RecTec 590/Stampede
HomeBrew Upright/Vertical Pellet smoker

W6YJ

  • Starting to taste the Smoke.
  • ***
  • Offline Offline
  • Posts: 221
Re: Any electricians here? 3 Phase question.
« Reply #9 on: November 21, 2020, 11:10:13 AM »


I was looking at the wiring diagrams and saw the jumpers. The used one i found the guy says it is 3 phase, I wondered if I bought it I could reconfigure the wiring going adding jumpers or if I could figure out how to make something to run it off the single phase wiring in the building.
It is about a 2 hour drive to where it is at. It may be wise to see if there is a serial number and then call Bakers pride and question them on how it may be wired. I had not thought of that until now.

You're on the right track WRT calling Bakers Pride.
They should confirm that it is just a matter of connecting the oven per their diagram.
 
Logged

Mikro

  • Starting to taste the Smoke.
  • ***
  • Offline Offline
  • Posts: 223
Re: Any electricians here? 3 Phase question.
« Reply #10 on: November 21, 2020, 12:19:54 PM »


>snip<

 A VFD won't help you in this case.

>snip<
Thanks for the clarification, when I suggested the VFD I was leary that it would not work for that application. :) That would not rule out a rotary phase converter though if needed. Very expensive though. :)
MK
« Last Edit: November 21, 2020, 12:30:33 PM by Mikro »
Logged
Firecraft Q450
RecTec 590/Stampede
HomeBrew Upright/Vertical Pellet smoker

hughver

  • Friends Want you to cook way to much.
  • ******
  • Offline Offline
  • Posts: 2198
  • University of Louisiana
Re: Any electricians here? 3 Phase question.
« Reply #11 on: November 21, 2020, 02:04:16 PM »

I believe that most homes in the U.S. have two single phase 120V lines coming into the house and the two lines are out of phase with each other. Commonly referred to as 220V, it is normally used for ovens and dryers. It would be very unusual for a house to have 3 phase power since most home distribution panels are designed to accommodate 2 out of phase lines.  :2cents:
« Last Edit: November 22, 2020, 09:55:33 AM by hughver »
Logged
--Hugh -- Sun Lakes, AZ. Traeger Select W/SS4, BGE-L, Charbroil Inferred Gas, Smokey Mountain Vertical Gas

hughver

  • Friends Want you to cook way to much.
  • ******
  • Offline Offline
  • Posts: 2198
  • University of Louisiana
Re: Any electricians here? 3 Phase question.
« Reply #12 on: November 21, 2020, 03:03:48 PM »

Logged
--Hugh -- Sun Lakes, AZ. Traeger Select W/SS4, BGE-L, Charbroil Inferred Gas, Smokey Mountain Vertical Gas

1MoreFord

  • Using less gas.
  • **
  • Offline Offline
  • Posts: 75
  • Central Arkansas
Re: Any electricians here? 3 Phase question.
« Reply #13 on: November 21, 2020, 10:59:07 PM »

3 phase power is usually 230V or 240V(or 460/480V).  Single phase is normally 208V although commonly called 220V.  Electrical nomenclature is stupid at best. :2cents:
Logged
Joe

Falcon Mk V gas grill, OK Joe Longhorn - gone, CharGriller Akorn, Camp Chef SG24, Weber 22" OTG
Pages: [1]   Go Up